In Mike Holts Illustrated guide to Electrical Exam Prep (based on 2020) Shows the following question on page 172.
What size XHHW copper conductor can be used to interconnect 90 deg C rated power distribution blocks protected by a 400A overcurrent device serving a 320A continuous load?
The answer is 400 kcmill rated at 380A at 90 deg. C. I agree with the wire size given will be protected by the 400 A breaker. The concern I have with this is they did not provide an increase in wire size for the continuous load. This appears to be justified by the statement in figure 6-14, which states "A 320A continuous load at 100% is permitted on 90 deg. C. equipment terminals. Where is that in the code book?
I understand equipment that is listed as a continuous load may be used at 100% instead of 125% ( 210.19(A)1(a) Exception 2 but where do we get the permission to use 90 degree rated equipment for less than 125% of continuous load?
What size XHHW copper conductor can be used to interconnect 90 deg C rated power distribution blocks protected by a 400A overcurrent device serving a 320A continuous load?
The answer is 400 kcmill rated at 380A at 90 deg. C. I agree with the wire size given will be protected by the 400 A breaker. The concern I have with this is they did not provide an increase in wire size for the continuous load. This appears to be justified by the statement in figure 6-14, which states "A 320A continuous load at 100% is permitted on 90 deg. C. equipment terminals. Where is that in the code book?
I understand equipment that is listed as a continuous load may be used at 100% instead of 125% ( 210.19(A)1(a) Exception 2 but where do we get the permission to use 90 degree rated equipment for less than 125% of continuous load?