Are dry type interior transformer stands structuraly rated?
Mule
Oklahoma
We are installing a 75kva transformer in a ceiling on a building upright pole and the local maintanence tech is welding up a stand to set the transformer on. It weighs just under 600lbs....Im sure he is just "guessing" at the structural design. Are most installations done like this, or, are they engineered?
KevinVost
Las Vegas
If I read your post right, your installing a 75kva transformer in a ceiling on a welded support. I would recomend that an engineer look and sign off on or design the support for this item. On a side note, you said your installing this in a ceiling. Check 2005 NEC art 450.13 (B) - prohibits the installtion of transformers in hollow spaces if over 50kva.
nakulak
if it fails and injures or kills someone, your behind is on the line. . . so if there is an engineer on record for the job, send him a sketch of your intended design for review to relieve some of the liability. if you can figure out the design yourself, just allow a safety factor of two. jmho
LarryFine
Henrico County, VA
Electrical Contractor
Not a good start. Obviously, we agree with that. I'd be leery about engineering support of 100lb overhead. Then again, I've never welded.
...if there is an engineer on record for the job, send him a sketch of your intended design for review to relieve some of the liability.
I'd insist that the support and its engineering seal be a package, without you in the middle. Make sure its attachment to the post is included.
charlie
Indianapolis
. . . 2005 NEC art 450.13 (B) - prohibits the installation of transformers in hollow spaces if over 50 kVA.
I am concerned about part of Kevin's post that seems to be ignored. 450.13(B) Hollow Space Installations. Dry-type transformers 600 volts, nominal, or less and not exceeding 50 kVA shall be permitted in hollow spaces of buildings not permanently closed in by structure, provided they meet the ventilation requirements of 450.9 and separation from combustible materials requirements of 450.21(A). Transformers so installed shall not be required to be readily accessible.
It is obvious that the CMP is concerned about larger transformers installed in that position. You have a problem with ventilation, combustible materials, weight of the transformer, and probably the clearance requirements of 110.26. If you are insistent on doing this, I would definitely get an engineer's seal on a drawing plus the AHJ's blessing before proceeding. :smile:
Goroon
Often over looked and seldom enforced.:cool:
Here in My state, the mechanical code requires a seperate permit for the installation of ANY Electrical Equipment installation over 400 LBS. Seismic issues!
Mule
Oklahoma
This is a commercial building with a average ceiling height of 20-32ft. We are not installing it above a ceiling....or maybe I should have used the term "roof" instead of "ceiling"
The stand is not in my scope of work.....the client (maintenance tech) is installing the support...so I cant be responsible for it, I only supplied the physical dimensions and weight requirements.....However, you have raised a issue in my mind....THEY should set the transformer, NOT ME, because if I did it, I, set it on a un-sufficent, or underdesigned stand, leaving me liable
So, Im focusing on, "are these installations usually installed without engineering, or with?".......What's your experience?
Goroon
To Your Point.
Never with out an Engineer ! For Me ! I am responsible for MY Installation!
My customer gives me this electrical installation, I install it with out an engineer, I am responsible for it entirely.
Mule
Oklahoma
I agree in most cases, but Im on T/M and parts of this installation have used equipment and Im under the direction of the client, but I do have the power to refuse and they greatly respect that. We have open communication...
mdshunk
Right here.
I say, wait and see what he comes up with. It may end up being something you could place a Sherman tank on. You might be worrying for nothing. On the other hand, if you have doubts, just do everything but place the transformer until you can get someone, other than you, to officially deem the rack suitable for that transformer.
Fulthrotl
~Autocorrect is My Worst Enema.~
it's funny what concerns pop up in different people's minds.... on person
can be saying.... "not a problem, do it all the time", and another person
can say about the same thing "ACK!!!! RED ALERT! WE'RE ALL GONNA DIE!!"
most transformers can be ordered with factory designed wall mounts,
usually two big #12 mild steel angles that bolt to the transformer chassis
and have a couple 1/2" holes on the wall side to bolt to the wall...
i've seen 1 5/8" strut with a strut strap the size of the column, top
and bottom of factory mounts, so you've got a 600 lb load hanging
by two strut straps..... :-?:-? in california, no less....
i guess there are engineers mainly 'cause otherwise there are people
who think the following design is just fine...