Are metallic device boxes and cable allowed in dwelling air return?

Status
Not open for further replies.

emf10

Member
Location
Southeast PA
The space I'm talking about is the typical joist space cold air return found in dwellings. I thought metallic device boxes and metallic cable such as MC or AC are allowed in this space but reading the NEC 2005 handbook I have found a comment on this:

"The exception to 300.22(C) permits cable to pass through joist or stud spaces of a dwelling unit, as illustrated in Exhibit 300.21. The joist space is covered with sheet metal and used as a cold-air return for a forced warm-air central heating system. [highlight]Equipment such as junction boxes or device enclosures is not permitted in this location.[/highlight]"

but 300.22(C)(2) states:

"Equipment. Electrical equipment with a metal enclosure, or with a nonmetallic enclosure listed for the use and having adequate fire-resistant and low-smoke-producing characteristics, and associated wiring material suitable for the ambient temperature [highlight]shall be permitted to be installed in such other space unless prohibited elsewhere in this Code.[/highlight]"

btw what do they mean by the joist space being covered with sheet metal? Around here it's just drywall and studs or joists.
 
Last edited:
We typically build a little box around the device box with scrap pieces of 2x4 if the device must be in a stud bay cold air return. Boxing in the box effectively removes it from the environmental air space.
 
mdshunk said:
We typically build a little box around the device box with scrap pieces of 2x4 if the device must be in a stud bay cold air return. Boxing in the box effectively removes it from the environmental air space.

I wonder if that violates any HVAC codes by cutting down the airflow. Sometimes, though, I'm in an old work situation where I wouldn't be able to box it in.
 
emf10 said:
I wonder if that violates any HVAC codes by cutting down the airflow.
They do plenty of calculations, but they're not so tight that you can't have a boxed in device in a stud bay return or two. No big deal. Just don't go too crazy. It's normally only when the device layout must be a certain way, like to jive with built in furniture and cabinets, where you would do this. In most cases, you can figure out a way to just mount the box one bay over, left or right.

emf10 said:
Sometimes, though, I'm in an old work situation where I wouldn't be able to box it in.
Simple answer; you can't really put a box in there then if you don't want to do some collateral damage.
 