1) Pool panel 200' away from main panel. Using #3awg thhn in pvc:
Cmvd=2kil
Vd=2kil/cm
Vd=(2)(12.9)(100)(200)/52,633
Vd= 9.8037353
Voltage drop exceeds 3% so #2awg is to be used?
2) conduit fill.....1 1/4 would be the minimum size pvc for 4 #2 thhn?
Cmvd=2kil
Vd=2kil/cm
Vd=(2)(12.9)(100)(200)/52,633
Vd= 9.8037353
Voltage drop exceeds 3% so #2awg is to be used?
2) conduit fill.....1 1/4 would be the minimum size pvc for 4 #2 thhn?