Thanks that's a good point relating to fire stopping requirements. But aside from that, does the NEC require low voltage or fire alarm cables to be protected with a pipe sleeve when passing through concrete?
Thanks that's a good point relating to fire stopping requirements. But aside from that, does the NEC require low voltage or fire alarm cables to be protected with a pipe sleeve when passing through concrete?
There is very little in the NEC about fire stopping and nothing that I know of relating specifically to concrete. I seem to recall firestopping info in Art 300 but limited time prevents me from getting specific section
And now you mention fire alarm. Fire alarm cable require physical protection and treated differently from limited energy. Art 760 is not my strong area. So with fire alarm you may be required to have a sleeve.
I would sleeve anyway to protect cables from damage
And lastly, most fire stopping is inspected by the building dept.
...By fire caulk, I'm referring to what I believe is called bituminous caulk, which expands to seal when heated....
FromNEC:OR can these cables simply pass through a core drill and just be surrounded by fire stop?
300.4 Protection Against Physical Damage. Where subject to physical damage, conductors, raceways, and cables shall be protected.
There is a difference between embedding something in concrete and running through a bored hole in concrete...are the cables direct burial rated? If not, then when in concrete you need conduit... remember, concrete moves and it wicks moisture...
:thumbsup:FromNEC:
There is a difference between embedding something in concrete and running through a bored hole in concrete...
:thumbsup:
Need for physical protection is the answer to OP's question, unless firestopping the penetration applies, but he seems to not be concerned with firestopping and wanting a more general rule for passing through concrete.
It is not. If the hole is through a floor a certain distance above the floor might be considered subject to physical damage in nearly all cases.Thanks guys.
But can I push back a little, if conductors pass through a core drill through concrete why would the conductors not have physical protection? Stupid question, it's not like the concrete is going to collapse. Why would physical protection from a pipe sleeve be required here?