mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Where does it say receptacles are splicing devices meeting the requirements of 110.14 (B)? As I'm reading it every feed through would be none compliant.
110.14(B)Splices. Conductors shall be spliced or joined with splicing devices identified for the use
Art. 100 Definitions: Device. A unit of an electrical system, other than a conductor, that carries or controls electric energy as its principal function.
It would then go to the listing of the device.
So the device itself doesn't need a listing in that regard?
Single and duplex receptacles rated 15 A and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors may be used to feed a single set of branch circuit conductors connected to other receptacles on a multi-outlet branch circuit. These devices have not been tested for tapping off more than one circuit from the receptacle by utilizing both the side-wiring and back-wiring terminals on an outlet. Duplex receptacles rated 15 A and 20 A that are provided with break off tabs may have those tabs removed so that the two receptacles may be wired in a multi-wire branch circuit
300.13(B)
The UL White Book says they are.
Roger
It appears wrapping a single conductor around a terminal, after carefully removing insulation in the middle, is the only legal way to get more than one wire on a terminal..........
You mean, if you're wrapping the wire under the "-.Back-wire (screw-actuated clamp type) terminations with multiple wire-access holes..", yes.If you're wrapping the wire under the screw, yes.
If it's a pressure-plate terminal, it might be listed for two conductors.