Are Registered Electricians Responsible for NFPA 70E compliance?

Status
Not open for further replies.

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
I'm trying to get a 5-hour class approved by an adjoining State. The class is titled "Arc Flash and Electrical Safety - NFPA 70E 2021". It could also be titled "How to Interact Safely with Electrical Systems in Accordance with NFPA 70E, 2021 edition".
But the State has listed on their website that the only classes approved for electricians are based on NFPA 70, The National Electrical Code, and their administrator has advised me that there are no exceptions to what is written on their website.
I think it's a given that electrician's are responsible for compliance with NFPA 70E. OSHA recognizes the standard, and if you don't use that standard, then you need to be using something comparable.
But I can only make the recommendation to their Board based on engineering judgment, or common sense, and I don't want to shoot myself in the foot, so-to-speak, and ruin my chances of ever getting approval.
NFPA 70E is a National Consensus Safety Standard, and as such, is not enforceable by law, and it's not voted in by AHJs, as the NEC is by edition. Legal jurisdictions recognize NFPA 70E, but it's not codified as law.
Any suggestions or opinions are appreciated.
 
Georgia is pretty flexible on their continuing education requirements, I’ve had classes that had nothing to do with NEC, and covered erosion control and the like. For awhile Georgia required you to carry a “white card”, if I remember correctly. If you dug a post hole for a temporary, you were required to have that card. Got the card, never heard anything more about it.
 
Get a class approved on the safety rules in the NEC. Labeling, signs
, LOTO, fault current, arc flash, there is plenty to pull from
 
I don't know if this is germane but it seems to me that NFPA 70E training/compliance would only be required in jurisdictions that have adopted that document. Here in CA some companies and AHJs adopt it and many others do not. Our Cal-OSHA requires a written electrical safety plan but does not reference 70E, although 70E may meet that requirement.
 
Status
Not open for further replies.