My primary question is whether it's acceptable to install a 175A continuous rated meter extender in a 200A rated base and a 200A service panel main breaker.
The NEC states that Branch Circuit and and Feeder overcurrent protection must be 125% of expected load, or essentially derated to 80% of it's rating (ref. 215.3 Overcurrent Protection of feeders), but I can't find anything so clear on the sizing service entrance overcurrent protection. Article 220 Parts III and IV lump service and feeder overcurrent calculations in to the same methods, so it stands to reason that they'd have the same derating implied... it just doesn't say so for service breakers (that I can find)
UL489 (the standard used to List circuit breakers for branch circuit, feeder and service entrance overcurrent protection) states in 9.1.4.4 that "A circuit breaker, having a frame size of 250 A or greater, or a multi-pole type of any ampere rating rated over 250 V; and intended for continuous operation at 100 percent of rating, shall be marked:
?Suitable for continuous operation at 100 percent of rating only if used in a circuit breaker enclosure Type (Cat. No.) ____ or in a cubicle space ___ by ___ by ___ mm (inches)?. Equivalent wording shall be permitted. Location Category C. The blanks are to be filled in with the minimum dimensions."
Typical residential 200A service panel main breakers are not marked for 100% (verified on Square D QO and Homeline, Cutler-Hammer panels), so by omission of a 100% marking appear to require 80% derating.
It seems to me, therefore, that the maximum acceptable continuous load on a 200A service would be 160A, therefore using a meter extender rated for 175A continuous use should be acceptable. (note: UL 414 meter sockets and extenders standard allows for an intermittent rating of not more than 125% of the continuous rating with no testing required)
Is there any clear direction in the NEC that requires 80% derating of service breakers for the total load on the panel?
Would code prevent installing a 175A continuous meter extender in a 200A service?
Thanks!
Pete
The NEC states that Branch Circuit and and Feeder overcurrent protection must be 125% of expected load, or essentially derated to 80% of it's rating (ref. 215.3 Overcurrent Protection of feeders), but I can't find anything so clear on the sizing service entrance overcurrent protection. Article 220 Parts III and IV lump service and feeder overcurrent calculations in to the same methods, so it stands to reason that they'd have the same derating implied... it just doesn't say so for service breakers (that I can find)
UL489 (the standard used to List circuit breakers for branch circuit, feeder and service entrance overcurrent protection) states in 9.1.4.4 that "A circuit breaker, having a frame size of 250 A or greater, or a multi-pole type of any ampere rating rated over 250 V; and intended for continuous operation at 100 percent of rating, shall be marked:
?Suitable for continuous operation at 100 percent of rating only if used in a circuit breaker enclosure Type (Cat. No.) ____ or in a cubicle space ___ by ___ by ___ mm (inches)?. Equivalent wording shall be permitted. Location Category C. The blanks are to be filled in with the minimum dimensions."
Typical residential 200A service panel main breakers are not marked for 100% (verified on Square D QO and Homeline, Cutler-Hammer panels), so by omission of a 100% marking appear to require 80% derating.
It seems to me, therefore, that the maximum acceptable continuous load on a 200A service would be 160A, therefore using a meter extender rated for 175A continuous use should be acceptable. (note: UL 414 meter sockets and extenders standard allows for an intermittent rating of not more than 125% of the continuous rating with no testing required)
Is there any clear direction in the NEC that requires 80% derating of service breakers for the total load on the panel?
Would code prevent installing a 175A continuous meter extender in a 200A service?
Thanks!
Pete