Good afternoon I apologize for being somewhat vague because this is a government building and no cell phones and pictures are allowed kind of deal.I was asked along with my boss to look at a 125V D.C. system after the company i work for installed two small small systems.The head electrician at this site though our new systems had something to do with the problem to be had.So to the issue the building has a battery bank and two chargers running essential systems 52 cells at 2.5VDC.The head electrician there tests voltage on the bank monthly.He says the two chargers show a fault of "+ ground" on a warning light.He showed us how he checks it and it he checks from terminals to the bare bonding wire to the rack witch is welded to the floor and so on redundant bonding.Today he showed us 124v to- and 6v to + for a total of 130v 52*2.5=130.He then stated he normally gets 60 something on - and 60 something + :? and that is the way its been for years so we disabled our to systems and re checked the fault on the charger still stayed and had reads of 124v to- and 6v to + so anyway no fault seen in our additions but in my head I cant understand how or way the voltage would have ever been split 50/50 across the two or why the 124v to ground on the and six on the other.The only thing i can think of is there is voltage bleeding through some on the conduits and retuning the only way it can through metal floors pipes and racks?