Are These Feeders Overfused ?
ramsy
NoFixNoPay Electric
LA basin, CA
Service Electrician
50+ year old 125A meter center, with #10cu on 40A breakers
* Was the 83% factor ever allowed for 40A feeders, similar to NEC 310.12 for =>100A feeders ?
* Were #10cu feeders @ 75C allowed at their 35A rating, some time before T.310.16 foot Note: referenced 240.4(D) for small conductors ?
Not to mention derating for eight (or seven) CCCs in a single conduit.
Yes, now that you mention it, the ampacity is only good for 28 Amps, with 7-9 CCC's
1" raceway can handle fifteen #10cu THHN
With 120v to ground, the bonding busing may not be required
There have rules for reduced size dwelling unit feeder and service conductors in the code for a long time. In the past it was just a table without any reference to 83%.
The oldest code book I have is the 1975. In that edition, the rule was found as Note 3 to Tables 310-16 through 310-19. Like now, the rule started at 100 amps.
Do the feeders in the picture carry 100% of the dwelling unit load? c
Yes, each dwelling with 240/120 sub-panel, & full kitchen.
Thanks for checking the 1975 NEC.
Ampacity for small conductors were also stuck at 60C ratings in the 1951 NEC, when rubber & thermoplatic insulation types were in use.