According to both NFPA780 and IEC 62305-3 you need a minimum distance from the LPS to be exceeded if you can avoid making equipotential bonding to other metalic structures in a building.
According to IEC 62305-3 (section 6.3) you need the double distance, if concrete is used as insulating material with reference to air. This international code is normaly used in Europe and Australia.
According to NFPA780 (section 4.21.2.4) you need half the distance, if concrete is used with reference to air. So it seems like US concrete is a better insulator...
Does other US codes consider the same as NFPA780?
Can anyone explain this difference between the two codes?