Are VFDs relevant when determining complinace with NEC 240.86(C)?

Status
Not open for further replies.
Does the NEC recognize the reduction (or absence) of motor fault current contribution to the line side of a non-regenerative VFD w/o a bypass a contactor? It appears NEC 240.86(C) pertains to motor loads in general with no consideration of the controller type. Is that the general consensus?
 
Does the NEC recognize the reduction (or absence) of motor fault current contribution to the line side of a non-regenerative VFD w/o a bypass a contactor? It appears NEC 240.86(C) pertains to motor loads in general with no consideration of the controller type. Is that the general consensus?

That's how I would interpret it, since that meets the intent of the section, that no spinning load is injected back onto the bus.
 