Are you allowed to cut and remove part of the electrical pull box and weld back to make the box smaller?

Status
Not open for further replies.

zemingduan

Senior Member
Location
Philadelphia,PA
Occupation
Electrical Designer
The electrician proposes to cut 9" wide from the center of the electrical pull box and weld back together in order to make the existing pull box 9" smaller in width to accommodate a new fresh air duct in the shaft. Is it legal to do this? I think all equipment shall be UL listed or something. If you modified it like this by yourself, it's not legal to do so.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The electrician proposes to cut 9" wide from the center of the electrical pull box and weld back together in order to make the existing pull box 9" smaller in width to accommodate a new fresh air duct in the shaft. Is it legal to do this? I think all equipment shall be UL listed or something. If you modified it like this by yourself, it's not legal to do so.

It depends on the configuration and pipe sizes that are existing in the box. If he shortens it then there may be a compliancy issue.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I have field modified many boxes. Unless they fall under 314.15 there is no NEC requirement for boxes to be listed. I have also had metal fabricators custom make boxes.
I agree. Back in the day it was routine to fabricate wireways and large J boxes. As Dennis mentioned, the OP just needs to be sure the box dimensions still meet Art. 314 dimensions.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Boxes are field modified all of the time and as mentioned often boxes are custom made. I don't see an issue with it. Similarly metal wireways are cut and modified all of the time because they typically come in fixed lengths.
 

kwired

Electron manager
Location
NE Nebraska
Boxes are field modified all of the time and as mentioned often boxes are custom made. I don't see an issue with it. Similarly metal wireways are cut and modified all of the time because they typically come in fixed lengths.
Yes, usually in 12 inch increments. If running to a corner then turning around the corner you about need to modify part of it to make it fit in 99%+ of most instances. Same reason you cut 10 foot lengths of raceway to fit a particular location.
 

zemingduan

Senior Member
Location
Philadelphia,PA
Occupation
Electrical Designer
Thank you all! Very helpful and I always learn something new from this forum. Engineer really needs to know more about how the electric is installed and constructed in the real world!
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thank you all! Very helpful and I always learn something new from this forum. Engineer really needs to know more about how the electric is installed and constructed in the real world!
You're welcome. It nice to hear several opinions on a subject.
 

jap

Senior Member
Occupation
Electrician
I'll be the bad guy.

Factory boxes looks good.
Even home made fabricated boxes look good.
Factory boxes that have been cut welded back an repainted has never looked good to me.

JAP>
 

kwired

Electron manager
Location
NE Nebraska
I'll be the bad guy.

Factory boxes looks good.
Even home made fabricated boxes look good.
Factory boxes that have been cut welded back an repainted has never looked good to me.

JAP>
That might depend on how good the person welding is at that task.

If you ever worked in food manufacturing places that utilize sanitary stainless piping systems there is someone there that can make modifications to a stainless box and polish it when all done and you probably will have a hard time telling where he made the changes. Painted or galvanized enclosures do require more finishing techniques though.
 

jap

Senior Member
Occupation
Electrician
That might depend on how good the person welding is at that task.

If you ever worked in food manufacturing places that utilize sanitary stainless piping systems there is someone there that can make modifications to a stainless box and polish it when all done and you probably will have a hard time telling where he made the changes. Painted or galvanized enclosures do require more finishing techniques though.

That person is usually me.

JAP>
 