I don't see why a laminate beam is so much different then the old method of pancaking 3 2x10 together to make a beam. We always drilled them.
We had one in a garage and the plumber and I each needed to dill a 3/4" hole to get across to the other side. I called the engineer and he said go at it. It depends on the size etc. I always try and drill them over a wall so there are no big issues.
It is not much different - you have to be careful where you drill either one or you will weaken it, same with truss frame members.
sometimes you can drill almost anyplace you want if the hole is not too large
But then I remember something about only towards the ends of it?
I was always told never to. But then I remember something about only towards the ends of it?
Also can you recommend books a electrician must have besides the NEC, IBC?
Thank you.
As long as you stay out of the middle 1/3 have at it...... I questioned an inspector on this issue and it is not a problem. If you drill multiple holes I believe they can be no closer than 2" apart. A manufactured truss would be an issue. Drill a hole and you could be paying for an engineer to make a recommendation.
You should look at my link.
Thanks for the pdf. I stand corrected, a laminated beam and a TJI joist are two different beasts.
When they first came out we had to have a PE sign off on drilling through one.
We all know know that they are more stable that regular lumber. So it was just not allowed to 'alter' them in the beginning.
Here is one example of how and where to drill. PP 36.
http://www.ilevel.com/literature/TJ-9000.pdf
You should note that the drilling point(s) are different than dimensional lumber. The 1/3 and 1/3 rule.
You can drill a I-truss not a 'normal' lumber truss.
Again you must know the manufacture to know where to drill or notch.
Are you allowed to drill through colums?
Here is another one: http://www.rosboro.com/pdfs/S560E.pdf
It would be good to include this type information in apprentice courses.