ayelsea

Member
Location
california
when calculating the electrical demand for lighting and/or receptacles (based off of sq. ft.), is the area measured from the inside of the walls, or are we supposed to include the thickness of the walls? i don't see anything in the nec that addresses this.
 

takelly

Member
Location
South dakota
220.12 Lighting Load for Specified Occupancies. A unit load
of not less than that specified in Table 220.12 for occupancies
specified shall constitute the minimum lighting load. The floor
area for each floor shall be calculated from the outside dimensions
of the building, dwelling unit, or other area involved. For
dwelling units, the calculated floor area shall not include open
porches, garages, or unused or unfinished spaces not adaptable
for future use.
 

ayelsea

Member
Location
california
220.12 Lighting Load for Specified Occupancies. A unit load
of not less than that specified in Table 220.12 for occupancies
specified shall constitute the minimum lighting load. The floor
area for each floor shall be calculated from the outside dimensions
of the building, dwelling unit, or other area involved. For
dwelling units, the calculated floor area shall not include open
porches, garages, or unused or unfinished spaces not adaptable
for future use.

thanks takelly.

so clearly the lighting area is measured from the outside of the walls. it does not state that the receptacle areas (for banks and office buildings, 1 va / sq. ft.) is to the outside of the walls also, but i would have no reason to assume otherwise, so i'll go with it. i have a feeling the 180 va per duplex will be the larger (and governing) of the two anyways.
 

ayelsea

Member
Location
california
regarding the lighting loads, nec table 220.12 does not have restrooms or anything like it. another document that i have (from iesna) for recommended illumination levels indicates 300 lux at the floor for restrooms, 300 lux at 3 ft. above floor for classrooms, and 400 lux at 3 ft. above floor for offices. so from this (considering all of the lights are the same efficacy), i can derive that the restroom lights should require a little more power than a classroom and around the same (or a little less) power as an office. nec table 220.12 indicates that schools (i.e. classrooms) are 3 va/ft while office buildings (i.e. offices) are 3 1/2 va/ft. so, in consideration of the above and for the purposes of determining the lighting load, i am going to lump the restrooms in with the offices. unless of course, somebody informs me that this is incorrect. btw, this is for an addition to an existing building, and i only need to know the electrical demand of the rest of the building in order to ensure that the main electrical panel is big enough to handle the addition and existing areas.

if anyone cares, just a little background on myself. basically, i am an architect trying to expand my competence. i currently work with and have worked much in the past with many consultants/specialists/engineers, but i have always liked doing incidental engineering myself. so right now i want to focus on electrical engineering. you will see that i am not quite an electrical engineer (more the generalist), and i am actually still getting used to the nec and have an awful lot to learn, but i feel i have a good foundation to be able to tackle this and eventually do it all on my own (until then, of course i will work with my consultants, but the more i take the lead, the better).

i'll be happy to share any knowledge i may have also.

i know there are many very knowledgeable people around here, so feel free to set me straight if anybody thinks i'm going astray... any comments are always welcome.
 
Last edited:

mgookin

Senior Member
Location
Fort Myers, FL
You mentioned schools. If you ever do a school, check OSHA requirements for light levels at desks. I know it sounds weird but at least around here OSHA prescriptive light levels have to be met at student workstations. The board of education adopts their standards to comply with disability requirements.
 

ayelsea

Member
Location
california
You mentioned schools. If you ever do a school, check OSHA requirements for light levels at desks. I know it sounds weird but at least around here OSHA prescriptive light levels have to be met at student workstations. The board of education adopts their standards to comply with disability requirements.

thanks, i will check that out.

here in california, all school projects must be approved by the DSA (division of the state architect), and rest assured they are on top of any required illumination levels, especially if it has to do with accessibility. the big thing here is energy efficiency too, and it is not always easy to reach the minimum illumination levels while remaining within the max. power demand.
 