bobby mercier
Member
- Location
- Saint-Georges, Quebec, Canada
How to not make the armor and the armored cable bounding conductor in parallel with the neutral when an armored cable is installed between a meter can and a service entrance?
No matter what you do it will be in parallel with the neutral. It would be the same if a metallic raceway was used. The NEC allows it. I don't know about the CEC.
That's true but in the case of an metallic raceway the parallel path is unavoidable and accepted by NEC.
On a side note, however, if you are speaking of AC cable, I don't see it as an acceptable wiring method for service conductors in 230.43
Maybe it could be a good idea to connect the bounding conductor just at one end and to remove the bounding device in the armored cable connector at one end to. That way bounding conductor and cable armored won't be in parallel with the neutral....
How far is the meter from the service disconnect?