Armored cable

Status
Not open for further replies.

herreraji

Member
One of my customers wants 12 ft of aluminum metal clad cable to connect a battery charger to the power source. He also wants the cable to terminate in a Hubble type 3-phase, 4-wire plug. The three conductors and the ground wires in the cable are #10 and the source is 480 V AC. Is this allowed by the Code?

Thanks,

Jose
 

herreraji

Member
Re: Armored cable

Originally posted by ron:
I don't understand the installation. Is the battery charger 480 3 phase input? What does the plug do? Is there a normal supply for the charger?
The charger input is 480 3-phase. The customer wants to plug the charger to a wall outlet via an aluminum metal clad cable.

[ April 13, 2004, 12:04 PM: Message edited by: herreraji ]
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Armored cable

Ah, OK. No, MC cable is not listed for that use and I certainly wouldn't use it that way. I assume he is concerned about damage. I can tell you that a severe- use rubber covered cord will outlast that MC many times over, it crushes very easily. Roll something over that MC (or even step hard or bend it sharp) and it's history as well as a danger. That's 480 volts! :eek:

-Hal
 