Seandb
Member
- Location
- South Africa
Hi all, I am a fiber optic technician (feel free to ask me about that stuff) and I am in a situation where we have an existing installed Corrugated steel tape (CST) fiber optic cable. The area experiences high levels of lightning damage, and this is clearly due to the previous installer NOT grounding or bonding any of the cable anywhere! Scary, but anyway, I am here to resolve the issue. I am familiar with NEC770:100 and we have implemented the bonding process already using 6AWG to bond the cables to each other. My question I need assistance with is the ends of the cables:
SECONDLY, at which point do I resort to installing an additional shielding cable above and parralel to the fiber, and do I gound that seperatley to the fiber or onto the fiber?
Please do not use acronyms in order for me to research the terminology easier.
- Do we ground to the buildings grounding arrangement?
- If not, is there a formula or calculation I need to use to design the grounding arrangement?
- The soil resistivity varies from 42ohm.m to 6000ohm.m
SECONDLY, at which point do I resort to installing an additional shielding cable above and parralel to the fiber, and do I gound that seperatley to the fiber or onto the fiber?
Please do not use acronyms in order for me to research the terminology easier.