Around four amperes on grounding conductors between CB panel and ground rods

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I was thinking a bad neutral on another service, but that current should just pass back to the transformer via your service neutral. Could be a utility issue with their primary neutral and that is causing current flow through the earth.
 

John A

Member
Location
New Jersey
Occupation
Inspector
As Don said in Post 2, a utility issue could be the cause. There was an issue a few years back in my neighborhood with 'stray voltage' which was determined to be the utility using SWER primary. Single Wire Earth Return that was feeding the pole mounted transformers. Basically 1 'hot', and a #6, or #4 down the pole to a ground rod at each pole.
 

retirede

Senior Member
Location
Illinois
As Don said in Post 2, a utility issue could be the cause. There was an issue a few years back in my neighborhood with 'stray voltage' which was determined to be the utility using SWER primary. Single Wire Earth Return that was feeding the pole mounted transformers. Basically 1 'hot', and a #6, or #4 down the pole to a ground rod at each pole.

I don’t think SWER is used anywhere in the US. You likely observed an issue with the utility’s primary neutral which caused it to behave similar to a SWER.
 

John A

Member
Location
New Jersey
Occupation
Inspector
retirede
The 'SWER was determined by the utility, and a few 'outside' engineers. This was about 15 years back. There was a lot of 'testing' and when a cut-out was opened on the primary, the stray voltage was gone. It was 'old' distribution that was not updated.

This info I picked up from a few utility linemen, and two of the engineers that were involved.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Would you mind elaborating on what you mean a little more?

If this is residential and you confirmed everything is bonded to the GECs properly then it seems to be stray from somewhere else like leakage from underground lighting, the power utility, or maybe the communication utility.

If this is a commercial location, then there could be much more going on.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
You will never get rid of it no matter how hard you try, because of MGN system that the utilities use !
 