Art. 110.34 Working Space & Guarding

Status
Not open for further replies.

boat64

Member
Location
Pennsylvania
Table 110.34(E) requires 9'6" elevation of unguarded live parts above working space: the question is; On an incoming 34 KV substation type transformer, with top bushing, feeding from a primary metering structure, with open wire, required to be a minimum of 9'6" to the top of the bushing?
Is the area below the top of the bushing considered "work space" given that the body of the transformer occupies this space.
 
Re: Art. 110.34 Working Space & Guarding

Check out engineering standards associated with the NESC.
 
Status
Not open for further replies.
Top