Came across section 215.2(A)(2) and wondered if it should be making reference to Table 250.102(C)(1) rather than Table 250.102??

Thoughts?


Sent from my iPad using Tapatalk
 
Came across section 215.2(A)(2) and wondered if it should be making reference to Table 250.102(C)(1) rather than Table 250.102??

Thoughts?


Sent from my iPad using Tapatalk

I think you mean 250.122. And no 250.122 is correct.

A service neutral/grounded conductor could be as small as an GEC, T250.66, but a feeder neutral/grounded conductor could be as small as an EGC, T250.122.
 