S srmoran Member Apr 2, 2006 #1 Is ground-fault protection required only in the main circuit breaker for 1000 amps and above? How about the branches with 1000amps rating. Are they also required?
Is ground-fault protection required only in the main circuit breaker for 1000 amps and above? How about the branches with 1000amps rating. Are they also required?
B benaround Senior Member Location Arizona Apr 2, 2006 #3 As long as the main has GPE than downstream feeders of 1000a or more are not required to have it.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Apr 2, 2006 #4 Except in hospitals, which require 2 levels of GFP on normal power.