Z Zane Bailey Member Jan 29, 2013 #1 Per condition 2, does this article prohibit a current setting above the amapacity of the cable when OC has adjustable trip settings?
Per condition 2, does this article prohibit a current setting above the amapacity of the cable when OC has adjustable trip settings?
JoeStillman Senior Member Location West Chester, PA Jan 29, 2013 #2 Some Conditions apply; The device is rated 800 amps or less The ampacity of the conductors does not correspond to one of the overload trip settings. The breaker does not have overload trip settings above its rating.
Some Conditions apply; The device is rated 800 amps or less The ampacity of the conductors does not correspond to one of the overload trip settings. The breaker does not have overload trip settings above its rating.