Has anyone had problems using rigid metal conduit or intermediate metal conduit as a equipment grounding conductor? I have a project that did not have the equipment grounding conductor installed between the main switchboard on the first floor and the step down transformers on the upper floors. The contractor already pulled the feeder cables between the main switchboard and the transformers.
The simplest fix would be to use the rigid metal conduit as a equipment grounding conductor however the people in charge of the construction supervision are saying that we should install a copper ground conductor. This is a more costly solution because it would require pulling out all the feeder cables between the main switchboard and transformers and then re-installing the feeder cables along with the copper ground conductor. They are saying that the copper ground conductor is more reliable. I'm saying that if it's in the NEC it's allowable, no questions. Opinions/Comments?
The simplest fix would be to use the rigid metal conduit as a equipment grounding conductor however the people in charge of the construction supervision are saying that we should install a copper ground conductor. This is a more costly solution because it would require pulling out all the feeder cables between the main switchboard and transformers and then re-installing the feeder cables along with the copper ground conductor. They are saying that the copper ground conductor is more reliable. I'm saying that if it's in the NEC it's allowable, no questions. Opinions/Comments?