I’m hoping for a little clarification on an issue that came up this week.
We finished a kitchen remodel rough in on a newer home and called it in for inspection. Getting new home runs to the kitchen would have required an conduit on the exterior of the home, so the HO, naturally, wanted us to try and use existing circuits. Luckily for us, the original electrician had 4 small appliance circuits plus, 20 amp DW circuit , 20 amp Disp circuit , 20 amp refer, 10/3 for the oven and 6/3 for the range. I was able to utilize the existing circuits for all the new stuff. The existing oven circuit (10/3) was no longer needed because they went with a free standing range, so I changed the breaker to a 2/p arc-fault and branched from it with two 12/2’s to feed a coffee maker and additional disposal.
The inspector didn’t call me on this, but said, “technically that is not legal according to 250.122(b).” In my opinion this article is clearly referring to voltage drop situations only and this inspector is interpreting this article incorrectly.
He says that the EGC needs to be #10. I’ve email with him quoting the article as well as the verbiage that follows it in the handbook, but he insists that his interpretation is correct.
This hasn’t been a contentious argument, and he’s been generaous with his time, but I don’t believe I’m wrong.
What say you?
We finished a kitchen remodel rough in on a newer home and called it in for inspection. Getting new home runs to the kitchen would have required an conduit on the exterior of the home, so the HO, naturally, wanted us to try and use existing circuits. Luckily for us, the original electrician had 4 small appliance circuits plus, 20 amp DW circuit , 20 amp Disp circuit , 20 amp refer, 10/3 for the oven and 6/3 for the range. I was able to utilize the existing circuits for all the new stuff. The existing oven circuit (10/3) was no longer needed because they went with a free standing range, so I changed the breaker to a 2/p arc-fault and branched from it with two 12/2’s to feed a coffee maker and additional disposal.
The inspector didn’t call me on this, but said, “technically that is not legal according to 250.122(b).” In my opinion this article is clearly referring to voltage drop situations only and this inspector is interpreting this article incorrectly.
He says that the EGC needs to be #10. I’ve email with him quoting the article as well as the verbiage that follows it in the handbook, but he insists that his interpretation is correct.
This hasn’t been a contentious argument, and he’s been generaous with his time, but I don’t believe I’m wrong.
What say you?