When sizing an EGC I use T250.122 and the OCPD for the branch circuit.
Option 1 : So a 80 amp OCPD needs a #8 EGC.
I was recently pointed to art. 25.122(D) in the last CEU class I instructed and was conviced that day that I was to use the overload sizing to calculate my EGC.
Option 2 : The overload neened is 51.5 amps and a #10 EGC.
After looking back today I read the part in the article; "but shall not be less than the size shown in table 250.122".
Option 3 : Now do I take the 51.5 amps and use T310.16 to determin a # 6 EGC and compare that to T250.122.



I like option 1.
Option 1 : So a 80 amp OCPD needs a #8 EGC.
I was recently pointed to art. 25.122(D) in the last CEU class I instructed and was conviced that day that I was to use the overload sizing to calculate my EGC.
Option 2 : The overload neened is 51.5 amps and a #10 EGC.
After looking back today I read the part in the article; "but shall not be less than the size shown in table 250.122".
Option 3 : Now do I take the 51.5 amps and use T310.16 to determin a # 6 EGC and compare that to T250.122.
I like option 1.