I am an instructor at the US Army Prime Power School and need clarification on Article 250.52(A)(7). The article states that grounding electrode plates shall expose not less than 2ft2 of surface to exterior soil. Does this mean that grounding electrode plates need to be 1'x2' thus 2 sq ft or will a 1' x 1' plate work with the idea that 1 sg ft of surface area on each side of the plate? I know this sounds silly but you'd be surprised at what students will argue about test questions.
 
As you've noted the requirement is for the amount of surface area in contact with the soil. That would include the top, the bottom and the edges. Here's the section:

250.52(A)(7) Plate Electrodes. Each plate electrode shall expose not
less than 0.186 m2(2 ft2) of surface to exterior soil. Elec-
trodes of bare or conductively coated iron or steel plates
shall be at least 6.4 mm (1⁄4 in.) in thickness. Solid, uncoated
electrodes of nonferrous metal shall be at least 1.5 mm
(0.06 in.) in thickness
 