I am wondering what the general consensus is with the following circles I've seen discussions go regarding this with Electricians, AHJs, and Engineers. Aux grounding electrode, or EGC is adequate? I am currently a fly on the wall between 3 parties arguing this (and I'm staying out of it for now) but its not the first time I've seen it come up so I was curious what others thought of this.
690.47 - This seems debated amongst people in my area but this says the EGC is adequate for bonding a detached carport structure (Steel/conductive). The debate as compared to a ground mount is that it is providing a separate covered structure for parking. Feel free to weigh into that.
250.32 (A) - Separate building, separate electrode. Goes to the point of the structure providing covered parking. It gives an exemption of a single branch circuit so lets clarify we aren't talking about that.
Scenario 1: Multiple Inverters with a combiner Panel
Scenario 2: Single or Multiple Inverters but with another single circuit serving lights affixed to the carport. This one seems to get people going. I've heard two arguments here: the lighting circuit further supports the concept that this is a separate functional building beyond just a "PV support structure." I have also heard that if the lighting is a single branch circuit, then it meets the exemption in 250.32 (A) and the PV doesn't count as a branch circuit.
In both scenarios we can assume its fed by a separately derived source because typically we are stepping up, but it would be behind an OCPD at the origination of the feeder (in the primary building structure) side so it shouldn't be a factor really.
Finally, regardless of what the code says, what do you think is best practice? Aux rod or not?
690.47 - This seems debated amongst people in my area but this says the EGC is adequate for bonding a detached carport structure (Steel/conductive). The debate as compared to a ground mount is that it is providing a separate covered structure for parking. Feel free to weigh into that.
250.32 (A) - Separate building, separate electrode. Goes to the point of the structure providing covered parking. It gives an exemption of a single branch circuit so lets clarify we aren't talking about that.
Scenario 1: Multiple Inverters with a combiner Panel
Scenario 2: Single or Multiple Inverters but with another single circuit serving lights affixed to the carport. This one seems to get people going. I've heard two arguments here: the lighting circuit further supports the concept that this is a separate functional building beyond just a "PV support structure." I have also heard that if the lighting is a single branch circuit, then it meets the exemption in 250.32 (A) and the PV doesn't count as a branch circuit.
In both scenarios we can assume its fed by a separately derived source because typically we are stepping up, but it would be behind an OCPD at the origination of the feeder (in the primary building structure) side so it shouldn't be a factor really.
Finally, regardless of what the code says, what do you think is best practice? Aux rod or not?