Help me with a bit of confusion here.
225.30 states a multi-wire branch circuit is considered a single branch circuit for the purpose of that section.
Then in 225.39(B) it states an installation of not more than two 2 wire branch circuits shall have a rating of not less than 30 amps.
and 225.39(A) states a single branch circuit can be not less than 15.
The way I read this, I can have one 15 amp (or 20) multiwire branch circuit feeding a outbuilding with say lighting on circuit A and receptacles on circuit B and use a switch as disconnecting means.
The 30 amp minimum would apply if I had two overcurrent devices in the outbuilding. (an example would be feeding a 240v well & a light)
I'm confused in that in scenerio "A" I do have two-2 wire branch circuits
so 225.30(B) leads me toward a 30 amp mininum, but 225.30 states that is considered one branch circuit.
225.30 states a multi-wire branch circuit is considered a single branch circuit for the purpose of that section.
Then in 225.39(B) it states an installation of not more than two 2 wire branch circuits shall have a rating of not less than 30 amps.
and 225.39(A) states a single branch circuit can be not less than 15.
The way I read this, I can have one 15 amp (or 20) multiwire branch circuit feeding a outbuilding with say lighting on circuit A and receptacles on circuit B and use a switch as disconnecting means.
The 30 amp minimum would apply if I had two overcurrent devices in the outbuilding. (an example would be feeding a 240v well & a light)
I'm confused in that in scenerio "A" I do have two-2 wire branch circuits
so 225.30(B) leads me toward a 30 amp mininum, but 225.30 states that is considered one branch circuit.