Anyone know of an example of exceptions 1 and 2 be it picture or website?

Been trying to picture one.

Also, where does it say in the code that you can only have one NM cable per opening in a NM box?
 
Chamuit said:
Also, where does it say in the code that you can only have one NM cable per opening in a NM box?

I don't know of an article that restricts you to 1 cable per opening, however the listing or instructions might.

314.(17) exception refers to single gang boxes less than 4" x 2?", and the last sentence allows multiple cable entries in a single knockout opening.
 
UL White Book said:
Boxes may or may not be provided with clamps. When clamps are provided,
the carton is marked to indicate the type of wiring system or combination
of systems for which they have been tested. The clamps are marked
with the following letters or combinations thereof to indicate that they are
suitable for use with nonmetallic sheathed cable ??N?? or flexible tubing
(loom) ??T.?? Clamps suitable for nonmetallic sheathed cable are also suitable
for multiconductor underground feeder and branch circuit cable where used
in dry locations unless the box or smallest unit carton is marked ??Nonmetallic
Sheathed Cable Only.?? Clamps have been tested for securing only one
cable per clamp, except multiple section clamps are considered suitable for
securing one cable under each section of the clamp, each cable entering a
separate knockout.

I think that last sentence does it. From page 248 of the UL White Book
 