I took the Mike Holt 25 question quiz HERE. I got a few more wrong than I would have liked, but afterwards I have been able to find the code that helps me arrive at the correct answers. I think I know why I got #10 wrong, but I'd like to verify.
Q10 The motor feeder conductor size for three 15hp, 208V, three-phase motors; three 3 hp, 208V single-phase motors; and three 1 hp, 120V, single-phase motors will be ________.
A. 2/0 AWG
B. 3/0 AWG
C. 4/0 AWG
D. 250 kcmil
I chose D but the correct answer is C. I used 430.24 but figured all three of the identical largest motors at 125% and the remaining motors at 100% and arrived at 277.35A which is 250 kcmil as per the 90C column of 310.16. If I only figure one the three identical largest motors at 125% and the remaining motors at 100% than I arrive at 254.25A which is 4/0 as per the 90C column of 310.16. So, I guess when a group of two or more identical motors are the largest, than I only figure one of them at 125% and the remaining motors at 100%. Is this correct? Thanks.
Roy
Q10 The motor feeder conductor size for three 15hp, 208V, three-phase motors; three 3 hp, 208V single-phase motors; and three 1 hp, 120V, single-phase motors will be ________.
A. 2/0 AWG
B. 3/0 AWG
C. 4/0 AWG
D. 250 kcmil
I chose D but the correct answer is C. I used 430.24 but figured all three of the identical largest motors at 125% and the remaining motors at 100% and arrived at 277.35A which is 250 kcmil as per the 90C column of 310.16. If I only figure one the three identical largest motors at 125% and the remaining motors at 100% than I arrive at 254.25A which is 4/0 as per the 90C column of 310.16. So, I guess when a group of two or more identical motors are the largest, than I only figure one of them at 125% and the remaining motors at 100%. Is this correct? Thanks.
Roy