The nameplate on an air handler reads min. circuit ampacity 50A max 70A. The question is do I have to size the conductors according to the maximum or can I size them anywhere in the range between 50 and 70A. Please back up your reply with a code article.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Conductor at least MCA, and breaker (or fuses, if spec'ed) no larger than MOCP.

That means you can use #6 or #8 wire, depending on type, and a 70a breaker.
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
The nameplate on an air handler reads min. circuit ampacity 50A max 70A. The question is do I have to size the conductors according to the maximum or can I size them anywhere in the range between 50 and 70A. Please back up your reply with a code article.

I would think that the 50A is the minimum circuit ampacity ( conductor size ) and the 70A is the maximum fuse size. Look at 430.52 since an air handler is a motor load. Size the conductors to a 50A load.
 