I have built a panel in a nema 4x box with no intention of it being in a classified area. Now i find out the area is classified. The box has fused terminal blocks with bussman GMA type glass fuses. The smallest fuse that is used in classified areas is bussman KTKR. It is filled and current limiting. These are to large.
The customer states i can use the glass (non-herm. sealed) type fuses in inst. circuit if i add a class 1, div. 2 switch prior to the panel. I am not so sure. He refers to NEC 2002, Art. 501.3 (5) fuses. This mentioned permitted as 501.3 (B)(1).
Please offer any interpretations.
I feel a spark is a spark in a classified area. I there is a fault on one of these 0.5a fuses (24vdc) it can cause a problem. Yes, the switch may help when changing the fuse but not if there is a fault.
Thanks,
Karl