art 514.8 ex 2

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Am I ready 514.8 ex 2 correctly. its permitted to install pvc and the last 2' can be RMC or IMC as it enters classified area?
 
After reading several post and re reading code. I find it hard to comply with 10' no union couplling rules but it does say #2 is an exception.
 
The exception does allow PVC for the underground with the last 2 ft IMC or rigid.
It's been a while since Ive done dispensers but you might check your specs. At one time some of the dispenser folks wanted metallic all the way.
 