M mannyb Senior Member Location Florida Occupation Electrician Mar 26, 2021 #1 Am I ready 514.8 ex 2 correctly. its permitted to install pvc and the last 2' can be RMC or IMC as it enters classified area?
Am I ready 514.8 ex 2 correctly. its permitted to install pvc and the last 2' can be RMC or IMC as it enters classified area?
M mannyb Senior Member Location Florida Occupation Electrician Mar 28, 2021 #2 After reading several post and re reading code. I find it hard to comply with 10' no union couplling rules but it does say #2 is an exception.
After reading several post and re reading code. I find it hard to comply with 10' no union couplling rules but it does say #2 is an exception.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 28, 2021 #3 The exception does allow PVC for the underground with the last 2 ft IMC or rigid. It's been a while since Ive done dispensers but you might check your specs. At one time some of the dispenser folks wanted metallic all the way.
The exception does allow PVC for the underground with the last 2 ft IMC or rigid. It's been a while since Ive done dispensers but you might check your specs. At one time some of the dispenser folks wanted metallic all the way.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 28, 2021 #4 I agree the rule allows pvc... But remember the burial depth is 24" not the typical 18" that is standard for pvc
I agree the rule allows pvc... But remember the burial depth is 24" not the typical 18" that is standard for pvc
W wallyworld Senior Member Mar 28, 2021 #5 PVC is used all the time, maybe even more with rigid at 30 bucks a stick. Sent from my SM-G950U using Tapatalk
PVC is used all the time, maybe even more with rigid at 30 bucks a stick. Sent from my SM-G950U using Tapatalk