art 514.8 ex 2

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Am I ready 514.8 ex 2 correctly. its permitted to install pvc and the last 2' can be RMC or IMC as it enters classified area?
 

mannyb

Senior Member
Location
Florida
Occupation
Electrician
After reading several post and re reading code. I find it hard to comply with 10' no union couplling rules but it does say #2 is an exception.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The exception does allow PVC for the underground with the last 2 ft IMC or rigid.
It's been a while since Ive done dispensers but you might check your specs. At one time some of the dispenser folks wanted metallic all the way.
 
Status
Not open for further replies.
Top