I need some clarification on 514.11 ('17 Code):
514.11(A) discusses emergency shut offs and states they shall be between 20 ft and 100ft from the fuel dispensers
514.11(B) states the device shall be readily accessible to the attendant.
In some of our "market" type stations the emergency disconnect is at the inside counter. Assuming this is allowable under 514.11(B) does this mean that disconnect must be within the 100' ?
A second question: 514.16 covers grounding and bonding and references 501.30.
501.30 does not accept double locknut or locknut bushing raceway connections back to the service. Does this preclude using PVC for those branch circuits (between seal-off and contorller/distribution panel) ??