cowboyjwc said:I would agree with barbeer. It's not required to have a redundent ground so you would not need to use hospital grade AC cable.
barbeer said:I agree it MAY fit 517.13(B) or it may not, we can make assumptions though. I would guess you cannot make "contact" with the equipment, in my mind it is above the ceiling?
Charlie, it is still in the "Patient Care Area" it is just not in the "Patient Care Vicinity"cpal said:How does one address the 6' beyond the perimeter of the patient bed location in this area??
Patient Care Area. Any portion of a health care facility wherein patients are intended to be examined or treated. Areas of a health care facility in which patient care is administered are classified as general care areas or critical care areas. The governing body of the facility designates these areas in accordance with the type of patient care anticipated and with the following definitions of the area classification.
RogerPatient Care Vicinity. In an area in which patients are normally cared for, the patient care vicinity is the space with surfaces likely to be contacted by the patient or an attendant who can touch the patient. Typically in a patient room, this encloses a space within the room not less than 1.8 m (6 ft) beyond the perimeter of the bed in its nominal location, and extending vertically not less than 2.3 m (71/2 ft) above the floor. [99:3.3.140]
roger said:John, how do you figure this doesn't need to meet the requirements of 517.13?
It is a treatment room so it is a Patient Care Area.
Roger
cowboyjwc said:we don't do hospitals here in CA
steve66 said:That's one way to cut back on health care costs. But what do you do with all the sick people?? Ship them to Nevada??
Steve
cowboyjwc said:Mexico.:smile: It's just as close and it's cheaper.
Guess I could have been more specific. The local AHJ's don't do hospital. We have state inspectors for that.
We only do outpatient clinics and denists.