An E/C working in a jurisdiction adjacent to mine is wiring a hospital operating room with isolated power supplies. He was asked by an inspector about a bond wire installed in the wall interconnecting the metal studs to the isolated power supply.
I knew of no such requirement. Have I overlooked something ?
 
An E/C working in a jurisdiction adjacent to mine is wiring a hospital operating room with isolated power supplies. He was asked by an inspector about a bond wire installed in the wall interconnecting the metal studs to the isolated power supply.
I knew of no such requirement. Have I overlooked something ?
Gus, this goes back to the days of flammable anesthesia and is no longer required.

Roger
 
Don't all metal surfaces need to be attached to a common ground bus?
And the common ground bus would be connected to an isolated power system 9if one is installed).
 
Don't all metal surfaces need to be attached to a common ground bus?
And the common ground bus would be connected to an isolated power system 9if one is installed).
Not in todays installations, this is covered in chapter 4 of NFPA 99 and unfortunately I do not have a copy available right now.

Roger
 
allow me to sneak a second question in here...
The FPNs at 517.160(A)(6) discuss the dielectric properties of the conductors used for this install. I have been asked if XHHW is superior to THHN in these applications, or is there another preferred conductor.
Any input ?
 
Gus, see the excerpt below from this SQ D technical paper


C. System Wiring and Conduit

The selection of a proper conductor is one of the most important design criteria of an isolated power system. If improper conductor insulation is chosen, the result is the same as if the capacitive leakage is raised. A good commercially available wire insulation for this application is cross-linked polyethylene, having a mineral filler instead of a carbon black filler. A minimum wall thickness of 2/64-in. should be
demanded for use in 120 V, 208 V, and 240 V applications. It is also important to specify wire with a dielectric constant of 3.5 or less, as recommended by the NEC and NFPA No. 99.

Standard Type THHN wire is definitely unsuitable. It can, however, be used for the ground conductor. The code demands that the #1 conductor in the system be color-coded orange, the #2 conductor color-coded brown, and the ground conductor color-coded green. In three-phase systems, the third conductor shall be color-coded yellow. Schneider Electric is often asked to specify manufacturers
and wire catalog numbers for the low leakage conductor. This is extremely difficult to do since the availability of these wires differs from region to region. Also, manufacturers have sometimes discontinued production of wire types that we have
recommended. The most accessible XLP wire has been low leakage wire #FR-XLP (VW-1 XHHW-2).

Recently, manufactures have rescinded their notation in their specs for XHHW and XHHW-2. This note referred to the recommendation found in the NEC (517-160) concerning the 3.5 dielectric strength. The different compounds used in the manufacturing of the insulation have changed or are subject to change, and the 3.5 dielectric strength may not be obtained. The XHHW and XHHW-2 insulation is still
the choice since it comes closest to meeting the recommendation. This is important to note since this could affect the overall installation of an isolated power system.

Roger
 
I am in awe ;)
Everytime I think I know a little something, someone like you shows up to teach me to be humble.
 