P pqualls Member Jul 8, 2009 #1 Does code require critical power 120 volt branch circuits to be installed in conduit (emt, imc,rgc) instead of hospital grade mc cable?(Nursing home project)
Does code require critical power 120 volt branch circuits to be installed in conduit (emt, imc,rgc) instead of hospital grade mc cable?(Nursing home project)
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 8, 2009 #2 The answer is pretty much yes, see 517.30(C)(3). 517.30(C)(3)(3) will give you some specific cases where you could use HCFC. Roger