Art. 645 UF cord & plug

Status
Not open for further replies.

80844u

Member
Provided that all the requirements of 645-2 are met, does Art 645 allow for non-plenum cord & plug from IT equipment to under raised floor receptacle (plenum space)? Although 645-5b approves the use of cord & plug, & 645-5d addresses the branch circuit requirements to the underfloor receptacle, it seems to only address the use of data cabling for under raised floor. Can you clarify this?
 

ron

Senior Member
Re: Art. 645 UF cord & plug

The cord installed below the raised floor must be "DP" rated per 645.5(D)(5). Essentially none are, so you can't place the cord below the floor.
 

80844u

Member
Re: Art. 645 UF cord & plug

That was what my thoughts were until I tried to figure out what a Type DP cable was, as I couldn't see it listed anywhere in the NEC. I found a UL sheet on the internet and it appears DP stands for data processing cable. So it seems that 645-5d5 address data cables only (and some of the cables listed are not plenum rated)

http://ulstandardsinfonet.ul.com/scopes/1690.html
 

ron

Senior Member
Re: Art. 645 UF cord & plug

DP rating is the outer sheath of a cable, traditionally for the power to data processing equipment, hence the name, DP.
It is a outer jacket type only identified by UL standards and required only by the NEC in 645.
 

ryan_618

Senior Member
Re: Art. 645 UF cord & plug

I don't understand why they would have to be DP rated.

The concept of allowing non-plenum rated cables in the IT room is that it has its own air handling system, and the room is not occupied by persons. Why wouldn't the code permit this? :confused:
 

ron

Senior Member
Re: Art. 645 UF cord & plug

If I recall, the reason the proposals were shot down, was the possible fire load below the raised floor may be higher without the special cable. But as pointed out, they let non-plenum rated comm cables below the floor, they require smoke detection below the floor, it's an isolated HVAC system, so it just doesn't make sense to use the fire load argument.
I also believe that rather than discuss the proposal, they referred it to NFPA 90, which also doesn't make sense since why would NFPA 90 have any control of text in the NEC?
 

sandsnow

Senior Member
Re: Art. 645 UF cord & plug

Here is a piece of Type DP cable. It was in a Info. Tech. Room. Sorry about the glare.

DPtypecableresized.jpg
 

ron

Senior Member
Re: Art. 645 UF cord & plug

Larry,
Excellent find. My understanding from speaking with many of the manufacturers, was that they didn't have a DP rating on their cables.
Do you happen to remember the manufacturer of the equipment that was connected to?
 

kevinware

Senior Member
Location
Louisville, KY
Re: Art. 645 UF cord & plug

Ryan_618: I don't understand why they would have to be DP rated.

I will learn how to use this form yet.......

Anyway, I work in a Information Technology environment and we purchase our cables from here:
PDU Cables
The cables are listed under UL83N4 as a "Electronic Data Processing Equipment" they work really nice. I give PDU Cables the specs and they manufacture the cables for me. Sad thing is I can buy all the equipment from the supply house to make the same product but if I were to make the cables then they would not be UL listed...Sounds like a racket to me but hey I am just an apprentice........JMO..

[ September 19, 2005, 08:27 AM: Message edited by: kevinware ]
 

ron

Senior Member
Re: Art. 645 UF cord & plug

Kevin,
It seems that the link you provided is for the branch circuit supply conductors in raceway covered by 645.5(D)(2)
The "DP" rated conductors per 645.5(D)(5) do not include the branch circuit supply conductors. The DP cables covered by 645.5(D)(5) are typically the cord and cap from the power strip to the receptacle.
 

kevinware

Senior Member
Location
Louisville, KY
Re: Art. 645 UF cord & plug

Thanks for the correction Ron. So if I am understanding 645.5(D)(5) correctly then the power strips that are installed in some of our network racks are in violation of this article. The power strips Tripp-lite are tie wrapped into the racks and the cord and cap is feed through the cut-out in the floor tile and plugged into my branch circuit. Am I correct that this is a violation??
 