Art 680 Bonding Perimeter Surfaces

Merry Christmas
Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
When attaching the pool shell to the perimeter bond at 4 points {680.26(B)(2)} it has always been required to use stainless fasteners (bolts, nuts, etc) to secure any lugs.
I was asked where the "no corrosive" requirement is located in the Code and can't put my finger on the specific wording. Any help ?
 

shortcircuit2

Senior Member
Location
South of Bawstin
When attaching the pool shell to the perimeter bond at 4 points {680.26(B)(2)} it has always been required to use stainless fasteners (bolts, nuts, etc) to secure any lugs.
I was asked where the "no corrosive" requirement is located in the Code and can't put my finger on the specific wording. Any help ?
In the 2023 Code the teminals are in 680.7(C)
Equipment is in 110.7
Then 110.2 approval
 