Good day,
I have an inspector in the Denver Colorado area who insists that all of my class 1, 2, and 3 circuits (50 volt and less) as described in article 725 must adhere to article 200.6 and therefore all grounded 24 volt systems negative or common conductors must have a continuous white or gray outer finish or a white or gray stripe.
This is not consistent with the industry standards or the control drawings that were provided me for installation.
I interpret Art. 725.3 "Other Articles" to say that only Art. 300 applies to Class 1, 2 and 3 circuits.
Can someone shed some light on this for me?
I greatly appreciate your time.
Kind Regards
I have an inspector in the Denver Colorado area who insists that all of my class 1, 2, and 3 circuits (50 volt and less) as described in article 725 must adhere to article 200.6 and therefore all grounded 24 volt systems negative or common conductors must have a continuous white or gray outer finish or a white or gray stripe.