I would like to see an example of an NEC Article 725 System, can some one post a link to a typical system.
There are lots of Class 2 systems
Also I found out that the typical 480V electrical unit heater (Markel) with a low voltage contactor, uses a Class 1 24 VAC control circuit. this means the thermostat can share the same raceway as the power, if the thermostat is wired with a Chapter 3 wiring method.
There are lots of Class 2 systems
Also I found out that the typical 480V electrical unit heater (Markel) with a low voltage contactor, uses a Class 1 24 VAC control circuit. this means the thermostat can share the same raceway as the power, if the thermostat is wired with a Chapter 3 wiring method.