Art gallery commercial track lighting

Status
Not open for further replies.

Sean Kane

Member
Location
Coconino Co. Arizona
Occupation
Electrician
The current lighting system has support cables in the electrical conduit with the conductors. This is stubbed out at the fixture. The conductors run to the fixture the support cables to frame. I'm pretty sure this is a code violation. What do you think. Thank you for your time. S.K.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I don’t have a code reference for you, but I’m picturing something similar to ceiling fans that have a support cable going through the down rod with the conductors, and being the instructions list to install this way, I would think your install falls under a similar scope?

Can you upload a pic ?


Sent from my iPhone using Tapatalk
 