Artical 517, Patient Care Facility, Wiring Method

Status
Not open for further replies.
Eye doctors office, eye exam rooms, are they considered a patient care area requiring the use of "Healthcare Facilities Cable" or is standard MC cable acceptable?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

Does the eye doctor perform eye surgeries and procedures or just prescribe glasses and contacts?

Chris
 
Eye Doctors Office

Eye Doctors Office

The offices are for examinations for prescribe glasses and contacts, no surgery.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The offices are for examinations for prescribe glasses and contacts, no surgery.

Ray

If there is no patient care treatment or examination other than to prescribe glasses or contacts IMHO I would not classifiy it as a health care facility.

Chris
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If this is a new facillity isn't this information in the design documents?

Roger
 

ksmith846

Senior Member
If this is a new facillity isn't this information in the design documents?

Roger

Ditto.....what do the plans state for those rooms?

I say if the plans do not state to wire per NEC 517 then ask the local AHJ what they think. Maybe they will determine that you need to utilize HG wiring and devices. Which, in turn, becomes a change order in your pocket.
 