517.11. Grounding of Receptacles and Fixed Electrical Equipment. In areas used for patient care, the grounding terminals of all receptacles and all noncurrent-carrying conductive surfaces of fixed electrical equipment likely to become energized that are subject to personal contact, operating at over 100 volts, shall be grounded by an insulated copper conductor. The grounding conductor shall be sized in accordance with Table 250.95 and installed in metal raceways with the branch-circuit conductors supplying these receptacles or fixed equipment.
Exception No. 1: Metal raceways are not required where Type MC cable, Type MI cable, or Type AC cable with an insulated grounding conductor is used.
Exception No. 2: Metal faceplates shall be permitted to be grounded by means of a metal mounting screw(s) securing the faceplate to a grounded outlet box or grounded wiring device.
Exception No. 3: An equipment grounding conductor enclosed in the sheath of a nonmetallic-sheathed cable assembly installed in accordance with the limitations of Sections 336-2, 336-3, and 336-4 shall be permitted to be used in accordance with Parts C and D of this article.