ibew441dc
Every wonder what the definition of a SHORT CIRCUIT was in the NEC?(I sure do)
Article 100-Part I and II should include an authoritative definition of the commonly used (and easily mis-used term).
Okay.....to avoid this part........I know, I know....see 90.1(C).blah, blah , blah...a trained person should know what a short circuit is.True, but based on what reference?, I challenge you to google it, check different dictionary's, IEEE, maybe NEMA even? My point is .....the different sources imply different things.
......A trained person should respect the fact that we all have to be accountable to an authority.........in the 'Electrical Installation World', that authority is NFPA 70(NEC).
The NEC states pretty clearly what an Overcurrent is and subdivides it into 3 categories.:smileand this is only one example)
Overload is in Article 100, Ground Fault is in 250,..... so where is SHORT CIRCUIT?
I suggest the NEC add Short Circuit, with an appropriate definition in Article 100, Parts I and II. Some might be saying......Well then make a proposal! I have never done it and wouldn't mind even if someone else made it.
Here is my suggestion....
Overcurrent. Any current in excess of the rated current of equipment or the ampacity of a conductor. It may result from overload, short circuit, or ground fault.
IBEW441DC said:Short Circuit-An intentional or unintentional, low impedance conducting connection, between any ungrounded conductor(s) establishing a difference of potential, or between any ungrounded conductor(s) and a grounded conductor.
FPN (1): A Short circuit is not a Ground Fault (see Article 250.2 Definitions)
FPN (2): A Short Circuit is not an intentional or unintentional electrical conducting connection between a grounded conductor and an equipment grounding conductor.(see 250.6 Objectional Current)