Article 110.26 Clarification

Status
Not open for further replies.

JefM

Member
In an industrial setting, a machinery control panel opens into an aisleway that has regularly scheudled production traffic (Forklifts, tuggers, etc. ) passing within 24" of the front of the panel. The supply voltage is 480V. Does this comply with the requirement to keep the working space in front of the panel 'clear and maintained' ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would say yes if there are no permanently installed parts of the structure that block the working space. The area certainly could be blocked off to provide the required working space.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Why avoid it? A used aisle way will help make sure the work space is not used as storage space or otherwise blocked.
 