450.13 Accessibility. All transformers and transformer vaults
shall be readily accessible to qualified personnel for inspection
and maintenance or shall meet the requirements of 450.13(A)
or 450.13(B).
(A) Open Installations. Dry-type transformers 600 volts,
nominal, or less, located in the open on walls, columns, or
structures, shall not be required to be readily accessible.
(B) Hollow Space Installations. Dry-type transformers
600 volts, nominal, or less and not exceeding 50 kVA shall
be permitted in hollow spaces of buildings not permanently
closed in by structure, provided they meet the ventilation
requirements of 450.9 and separation from combustible materials
requirements of 450.21(A). Transformers so installed
shall not be required to be readily accessible.