Z zachw45 Member Aug 10, 2004 #1 in this article it states that one 20a circuit can feed the whole bathroom as long as it complys with 210.23a. does everything have to be in 12ga wire now becuase of the 2o amp circuit or can 14 be tapped off for the lights and fan in the bathrooms.
in this article it states that one 20a circuit can feed the whole bathroom as long as it complys with 210.23a. does everything have to be in 12ga wire now becuase of the 2o amp circuit or can 14 be tapped off for the lights and fan in the bathrooms.
ryan_618 Senior Member Location Salt Lake City, Utah Aug 10, 2004 #2 Re: article 210.11 c 3 exception All must be number 12. See 240.4(D).